Strange... Bad Contact? Is the charging current changing a lot at Point2 and bad contact causes wrong Voltage Measurement? Did you maybe crosscheck with Voltmeter? |
Beta Was this translation helpful? Give feedback.
-
What's your balance voltage set at? I don't balance until cell voltages all hit 3.55 - I saw some odd behaviour when I set a lower balance start voltage (3.4) and I think one cell was at a higher state of charge than the others, causing some spikes in charge. Top balancing (balancing only when the voltages hit desired charge level) seems to be the way to solve this for LFP (my spikes have reduced, now I just need to spend longer in the absorption voltage for the balancing to have time to work) |
Beta Was this translation helpful? Give feedback.
-
Hello,
anyone of you saw already a similar cell voltage behaviour as I have?
The cell is first reaching max voltage, then the balancer (JKBMS) kicks in and balances the cell (1). After the cells are on the same voltage (2) then the cell is loosing voltage and is then balanced again until all cells reach the same voltage (3) again.
For me it would make more sense, if all voltage rise the same after reaching (2).
What are your opinions?